Seismic Design Option

Posted by Surabhi Tripathiover 2 years ago
Seismic Design Option

I am trying to design my Anchor Bolts for seismic loading, But I am getting an error message statement " THE CURRENT SEISMIC REGULATION (EN1992-4) DOES NOT COVER STANDOFF WITH GROUT APPLICATIONS, WHERE T>=0.5d", does this means that there can't be a gap b/w base plate and concrete slab in case of seismic design ? also is t the thickness of grout and d the dia of the anchor bolt ?, also what are the additional provisions to be considered in case of Seismic design , i.e. parameters that we need to define in PROFIS additional to Static design, how to select the seismic parameters in PROFIS?

Post installed anchors,seismic design of anchors

3 Replies
Posted by PARSHANT SHARMAover 2 years ago
Hello Ms. Surabhi, Thank you for asking an interesting question.You can design Seismic anchor design with grout but as per EN 1992:4 (design code for post installed anchors) the thickness (t) of the grout shouldn't be greater than or equal to 0.5x Anchor diameter (d).Example: For 16mm dia anchor, the maximum thickness of grout possible is 7 mm or less.The Profis Engineering Software gives you option to design Post Installed Anchors in Static, Seismic, Fatigue & Fire conditions (activate Profis by clicking here: PROFIS Engineering Suite - Hilti India ). Alternatively, you may raise design request to Hilti by clicking here: Anchor Design Services - Hilti IndiaI am also attaching copy of EN 1992:4 for your quick reference. Seismic design guidelines are Page 104 onwards.

Posted by Surabhi Tripathiabout 2 years ago

Hi Prashant, 0.5*d holds only when we are checking the shear capacity without lever arm , in case we have checked for shear capacity with lever arm(which accounts for additional moment acting on the bolts) we can we can provide grout thickness up to 40mm.


Posted by PARSHANT SHARMAabout 2 years ago

Hello Ms. Surabhi, Yes you can do so in case of Anchor design under static forces but not incase of Seismic forces as EN 1992-4 does not cover the standoff with grout applications, where t>=0.5d under seismic anchor design conditions.