Fire Compartmentation

I have one problem,In our site some areas we have cable penetration without containment. Plz provide me proper detail for that types of penetration how to seal and which Engineering Jujment we can used.

Passive Firestop,firestop,Fire selant,fire resistance,compartmentation

1 Reply
Posted by Karan Khannaabout 7 years ago

Hi Mr. Verma,

Thanks for posting your query.

Without a complete compartmentation, there is no possibility of fire-stopping a system. In such a case it will be simple sealing which can be done with any sealant, such a system will not have a Fire-Rating.
In case you need Engineering Judgement you have to ensure – that compartmentation is being achieved. Engineering Judgment (EJ) is not to compensate absence of Fire Compartmentation.

Based on a proper compartmentation and providing us the details as the following we will need to identify the nearest tested system to prepare the EJ.

  1. Opening Size
  2. Penetrant
  3. Thickness of Slab/Wall
  4. Fire Rating of assembly,


Please reach out to us in case you need any further support.

Regards,
Karan Khanna

firestop,compartmentation,Engineering Judgement

2 comments on this reply
Posted by Karan Khannaabout 7 years ago
Thanks for sharing the information. There are a few more details required from your end to provide the Engineering Judgement (EJ). I have shared the input sheet over mail. Please provide the same to proceed further.

Posted by Rishuabout 7 years ago
Opening size- 1500-1000mm 4 PVC insulated Cabel 35mm Wall thick - 250mm concrete wall Fire Ratting - 2 hours